Discuss dual RCD CU unusual tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
HELLO ALL

i am changing over a cu.

i have conducted basic testing before deciding to change over to a dual RCD wylex 17th ed board.

The board's RCDs and main switch were prewired.

The neutral cable comes out of one rcd and into another and out again from the same terminal and directly back to main switch.

Although i prefer to have the neutral wires fixed directly to the no protected neutral bar and from their to the main swtich i decided to go with the wylex set up.

with all mcb off i energize the board and one by one engineered both RCDs,
then started to energize each mcb.
However weirdly 4 out of 6 of the mcbs tripped the RCD which was not protecting them?

Is this a phenomenon that any one else has encountered?

Tomorrow i will retest each circuit to confirm integrity of insulation resistance and confirm no current leakage to earth and confirm i have wired all circuits correctly to each protected neutral bar.
Also Ill probably seperate the neutral cables and connected them all to the unprotect bar and then back to the main switch.

However i would like to know your ideas as to what may be causing this weird tripping?

thanks very much for you time in this matter.

DD368
 
Last edited:
All testing should have been carried out before attempting to install the board also check for borrowed neutrals between circuits as well , with all appliances unplugged and other equipment isolated , could you post a picture of the board internals ..
 
Bang test anyone? Hope you've not charged your customer for your mess up!

Weird tripping as you describe suggest you've got your circuits, RCD's and neutral bars mixed up!
 
Don't alter the factory fitted wiring inside the CU. Wylex have designed and tested the assembly in the configuration it was supplied to you and there is no reason for you to interfere with it.

The symptoms you have described are very common and exactly what you would expect from either incorrectly connected circuits or a N-E fault within the installation
 
HELLO ALL

i am changing over a cu.

i have conducted basic testing before deciding to change over to a dual RCD wylex 17th ed board.

The board's RCDs and main switch were prewired.

The neutral cable comes out of one rcd and into another and out again from the same terminal and directly back to main switch.

Although i prefer to have the neutral wires fixed directly to the no protected neutral bar and from their to the main swtich i decided to go with the wylex set up.

with all mcb off i energize the board and one by one engineered both RCDs,
then started to energize each mcb.
However weirdly 4 out of 6 of the mcbs tripped the RCD which was not protecting them?

Is this a phenomenon that any one else has encountered?

Tomorrow i will retest each circuit to confirm integrity of insulation resistance and confirm no current leakage to earthand confirm i have wired all circuits correctly to each protected neutral bar.
Also Ill probably seperate the neutral cables and connected them all to the unprotect bar and then back to the main switch.

However i would like to know your ideas as to what may be causing this weird tripping?

thanks very much for you time in this matter.

DD368

I'll have a wager on that one!
 
I had a fault on a new board a few weeks ago, done all my tests, happy with them,carried on and replaced the board. Then I had a reverse polarity on my socket circuit i was testing. Then after some head scratching even though my initial testing was correct,you start to over think it. haha

long story short,the manufacturer had assembled 1 rcd in reverse polarity. Simple remedy swap the feeds to correct polarity. Just goes to show they dont alway check there cu for polarity.
 
Thanks all....
I didn't alter any wiring but found a neutral to earth fault which made the RCD trip weirdly. Personally I think it's the way wylex wired up the box. Instead of each neutral from RCD going to the main neutral bar and then to the main switch wylex wired it so that RCD 1 neutral goes to RCD2 neutral and then out to neutral of main switch.
The current leakage came apparent after spots were reinstalled into the ceiling recess. I guess the builder was a bit rough when he put em back.
 
Last edited:
Glad you found the fault but those neutral links you describe are the feeds to the RCDs so perfectly ok and perform exactly the same function as the other configuration you mention.
 

Reply to dual RCD CU unusual tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
875
I've got a dual rcd mk sentry board that I want to inverter into an rcbo board. If I link the two neutral bars from the main switch is this OK to...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock