Discuss Earth fault loop impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Gardner

How does earth fault loop impedance and disconnect time requirements change for 3phase 3 wire 230 volt systems where the phase to earth voltage is 133 volts instead of 230 volts?
 
R= V/5In for a B type MCB. so you'd use 133V for the value of V.
 
Disconnection times only double to 0.8 s once the Uo decreases below 120V rms, so at 133 V rms the disconnection times will remain the same as for a Uo of 230 V.

However using Tel's formula above, decreasing Uo from 230 V to 133 V will reduce the impedance ( by a factor of 1.73).
So say for a 32 A type B BSEN60898 with a Zs at Uo of 230 V = 230 / 160 = 1.44 Ω
but for a 32 A type B BSEN60898 with a Uo of 133 V Zs = 133 / 160 = 0.83 Ω.
 
Disconnection times only double to 0.8 s once the Uo decreases below 120V rms, so at 133 V rms the disconnection times will remain the same as for a Uo of 230 V.

However using Tel's formula above, decreasing Uo from 230 V to 133 V will reduce the impedance ( by a factor of 1.73).
So say for a 32 A type B BSEN60898 with a Zs at Uo of 230 V = 230 / 160 = 1.44 Ω
but for a 32 A type B BSEN60898 with a Uo of 133 V Zs = 133 / 160 = 0.83 Ω.

Makes sense. Looks like I will have to increase the PE then. Would a full size 2.5mm2 PE sound right for a 20amp MCB at 30 meters?
 
no. you work out your actual Zs first. Ze+ ( R1+R2), then calculate the PEFC from I = V/Zs.

from a design viewpoint you could use the max. Zs for the breaker but be prepared for it to be higher if the actual Zs is lower.
 
Last edited:
You have a Ze value (lets say this is 0.3Ω). You are running a 30m long circuit from a 20A MCB type B to BSEN60898 at origin.
Your design voltage is Uo of 133 V.

PEFC(max) = Uo/Ze = 133 / 0.3 = 443.3 A
Adiabatic equation
adiabatic only.jpg
From the graphs in appendix 3, 443 A is off the graph so take the instantaneous trip value of 100A and a time of 0.1s, k = 115
minimum csa for the protective conductor is 0.27 mm².
However the minimum size csa for a conductor in a power circuit from table 52.3 is 1.5mm² therefore 1.5mm² is fine.
Then you need to calculate volt drop on 20A design current (max) on 30m of 2.5mm² line conductor and neutral conductor = 18mV/A/m *20A*30m = 10.8 V this is less than 11.5V max for power so you are OK.
 
You have a Ze value (lets say this is 0.3Ω). You are running a 30m long circuit from a 20A MCB type B to BSEN60898 at origin.
Your design voltage is Uo of 133 V.

PEFC(max) = Uo/Ze = 133 / 0.3 = 443.3 A
Adiabatic equation
View attachment 29333
From the graphs in appendix 3, 443 A is off the graph so take the instantaneous trip value of 100A and a time of 0.1s, k = 115
minimum csa for the protective conductor is 0.27 mm².
However the minimum size csa for a conductor in a power circuit from table 52.3 is 1.5mm² therefore 1.5mm² is fine.
Then you need to calculate volt drop on 20A design current (max) on 30m of 2.5mm² line conductor and neutral conductor = 18mV/A/m *20A*30m = 10.8 V this is less than 11.5V max for power so you are OK.

but not in OP's case as his line voltage is 133V so a max. VD of 5% is 6.65V.
 

Reply to Earth fault loop impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
483
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K
Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Replies
7
Views
1K
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
310

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock