Iv been given the scenario:
6 circuit earth fault loop impedance values were recorded. Each circuit has type B cb.
referring to the maximum values, show by calculation if these values are acceptable.
so I can't do zs =ze+R1/R2 because they've not provided me with ze.
doing some research it looks like it could be this calculation
Voltage/10= 230/10 =23
Devide that by the A rating of circuit = 23/32 (32A as an example) =0.719
Then times by 2 = 0.719x2 = 1.44
is that the correct way to approach this scenario?
Thankyou