craigswinton

Was wondering if any one could help me with wiring of an earth referance board. Have got 6 erb in different rooms supplied with a 16mmearth daisy chained between them from main riser. Each room has general sockets and power in it. How do you wire these circuits that are between rooms to the separate erbs in there correct rooms.
 
I think you will need to give a better explanation of what your doing. An ERB or earth reference bar is the central earthing point in medical locations.
 
I understand the purpose of the erb. It's just on our drawings we have got let's say a cleaners socket circuit in 3 rooms with 3 separate erbs on the wall in each room so just wondering how you would wire the earth between the rooms.
 
Have you read MEIGaN? Apologies if you know it! http://www.mhra.gov.uk/home/groups/comms-ic/documents/websiteresources/con2018069.pdf
I cant remember if the cleaners sockets need to be bonded back to the ERB but all the sockets used for medical equipment will need a separate cpc back to the ERB as will the lighting. I find it a bit unusual that the cpc's are daisy chained between rooms & ERB's, normally each ERB would have its own cable back to the main earth or distribution point.
 
I believe my site foreman has copy of the Meigan. We were also wondering about this as been trying to get information of folk on site has been difficult nobody wants to say what is the right thing to do. As why I have decided to join this forum in hope of some helpful information on it.
 

Reply to earth referance board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock