    I've just done an EICR on an install earthed TT . The Ze on the rod was high 245 ohms , which in theory is fine as it is less than 1667 and the equation Ra X 0.03 > 50v is satisfied .
    When the gas and water bonds are reconnected the Ze drops down to 4.4 ohms ,

    Do I put another rod in ?
    The property is in a built up area with pme available , do I get the Dno to fit pme ?
     
  2. telectrix

    telectrix Scouser and Proud of It Trusted Advisor

    it's the gas and water pipes bring down the Ze. rather than relying on that, a PME system would be advantageous.
     
  3. Andy78

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Yes an enquiry for pme would be worth it if the customer fancies the outlay. The measured ze would be worth a mention on the report, as would the less than desirable situation of RCDs providing fault protection where a viable and more reliable alternative exists.
     
  4. westward10

    westward10 Electrician's Arms

    Top Poster Of Month

    Location:
    Northamptonshire
    The rod resistance shouldn't exceed 200 ohms. It is nearly always the case for it to drop with the bonding connected due to parallel paths. This resistance could even increase in the drier months so yes I would try to look at PME.
     
  5. madmaz

    madmaz Regular EF Member

    Earthrod is unstable you can't rely on the fact that gas and water pipe bonding brings tears resistance down as metallic pipes may be replaced in future with plastic equivalents. Either install new rod or tnc-s enquiry
     
  6. davesparks

    davesparks Trusted Advisor

    Location:
    guildford
    For what reason should it not exceed 200 ohms?
     
  7. Wilko

    Wilko Gorillas are Great Electrician's Arms

    Location:
    Berkshire
    Hi - Table 41.5 note 2 has an observation that >200 Ohms "may not be stable", but that's all I've seen.
     
  8. HandySparks

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Ha ha! I was going to say the same, davesparks, but couldn't be arsed to take the flack or argue the to$$.
     
  9. 7029 dave

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    If 200 ohms is stable, much better than the ra all over the place,with an earth to earth system which TT is, stability is key.
     
Loading...
Similar Threads - Earth rod bonding Forum Date
Main bonding made to separate earth rod? Electrical Forum Feb 22, 2017
Pete's Videos How to install an earth rod, or not as the case maybe Electrical Forum Sunday at 11:55 AM
Pete's Videos All you need to know about fitting an earth rod Electrical Forum Feb 12, 2017
Can you earth to ground rod with bigger earth cable than the tails ? Electrical Wiring, Theories and Regulations Jan 13, 2017
Unprotected and damaged Earth to Electrode - C2 or C3? Periodic Inspection Reporting & Certification Dec 29, 2016
Do you need an earth rod for an outbuilding? Electrical Wiring, Theories and Regulations Oct 31, 2016
How Far Out From House To Locate Earth Rod? Electrical Forum Aug 27, 2016
A Guide To Earth Electrodes & Testing Electrical Forum Aug 23, 2016
EV Charging & Earth rod's Electrical Forum Jul 13, 2016
Domestic TT earthing system second rod Electrical Forum May 10, 2016
Electricians Directory Post a Domestic Job Post a Commercial Job