Discuss Earthing and voltage issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

daiplayer

Hi all

Having a strange problem with some testing .

Did an installation for somebody and upon testing discovered high Ze . ( 640 ohm )

Not happy with result ( after testing all other earthing conductors to infinite ohm or higher than 640, bonding no doubt), i discovered the earthing conductor was not connected to an earth rod, neither is there a rod to be found.
ok....so replace earth rod and conductor .

However im also getting some funny voltages accross the board. I did some ir testing to see why it is that somebody has discconected the earth ( possible earth fault ) , all good other than one mcb . Mcb of course was off ( as were all the other plus the main switch) however i was picking up flucuating voltages between the L ( at the top of the breaker which was off ) and earth of 105v , 50v, 96v , 12v, and kept on fluctuating .

The supply voltage seems fine L-N , 230Vac.

I cant understand why there could be voltages appearing on the earth or the live to the breaker when the dp main switch, rcd , all mcbs, were off ? any ideas ?
 
thats what im wondering , dodgy tester ? :-/ , however it only seems to do it on this one single circuit. . could dodgy batteries do that then ?
 
try using an analogue voltmeter/multimeter. and what's the Ze now you have reinstated the earthing?
 
Yeah if there is a broken earth then your digital meter will pick voltages up like that. Think it's called capacitive coupling.
 
Yeah if there is a broken earth then your digital meter will pick voltages up like that. Think it's called capacitive coupling.

Well thats a new one on me ....:) as they say , learn something new everyday. :)

- - - Updated - - -

Or, put a 230V lamp in parallel with your Digital meter.

i did that yeah. i did it with the multifunction, then with my fluke voltage indicator , and it showed the same.
 
ok further note..... wandering around the board with my voltage indicator, testing everywhere for funny voltages.

Tested between the incoming N, ( top of dp switch) and the m.e.t. .......and shows continuity.....

why would this happen ???
and before people scream TNCS ! , i did a loop test L,N, and the m.e.t. to rule this out. and shows 343 ohm. im guessing two parallel bonding conductors through the pipework .
 

Reply to Earthing and voltage issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
770
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock