Discuss Eicr Code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

graham123

6mm singles from 100a TP 60947-2 in a main panel to an adcent enclosure to a 16a 60898-D Tp, then 6mm leaving this to air con units. Would you code 2 the 6mm singles from the 100a 60947-2? As exceeds current carrying capacity?. Or because the 6mm singles are less than 3 metres to the enclosure no code?
 
On the face of it no code, however are they single insulated/sheathed ?. or double insulated/sheathed ? and are they accessible outside of the enclosures ?, or are they in containment between the enclosures ?
 
No code.

I would be checking the incoming/outgoing terminations at the 60947 if there were other cables also terminated and the 6mm was just stuffed in with them. Are they tight/secure? Have they been tinned or had ferrules applied?

If all good in your professional opinion, proceed to next inspection :)
 
Thanks for the replies, I am also wondering what you guys would put for these. No visible bond to Ventilation ducting system from the met. Continuity test between met and ducting 0.01. Put it down as a C3 as their is nothing visible but continuity is acceptable. Also should the lightning conductor pit be bonded back to the met? C3?
 
are you sure your continuity measurement isnt the R2 of any connected equipment? fans ect, is the ducting actually extraneous?

no expert but some LPS systems are bonded some arnt depends on what the designers of it want.
 
It could be that the structural steel (which is, or should be already bonded) is utilised as the effective bonding conductor, see 543.2.1 part (vii) and 543.2.6

The LPS, as above, depends on the design
 

Reply to Eicr Code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
798
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock