- Reaction score
- 685
Your input please, normally I just make a list of faults and a bright young office thing types up the report and allocates the codes (I think i'm deemed too old and the bright young thing has a degree and the latest version of the test and inspect and a winning way with people and a higher salary then me - but I digress)
Young thing is on holiday, I have had to input my own data for once, but I admit i'm out of touch. What codings would you give:
undersizes tails
old rewirable fuse board
no rcd protection
6mm bonding
no fan isolator in bathroom with no window
bathroom fan 240V in zone 1
shower has had notch cut in case at top and the cable surface mounted (loose) fed straight in the top
spur for gas boiler taken from the immersion tank radial
I was leaning towards a C3 for all of these, your input please.
and on a different job I have SWA feeding a RCCB which feeds some H07 flex, the swa is protected by a 60947-2 with the disconnection time of 0.4 giving a maz reading of 0.19. The readings at the rccb are within tolarance, but at the end of the H07 are not. As the H07 is protected by the RCCB do I need to worry?
Young thing is on holiday, I have had to input my own data for once, but I admit i'm out of touch. What codings would you give:
undersizes tails
old rewirable fuse board
no rcd protection
6mm bonding
no fan isolator in bathroom with no window
bathroom fan 240V in zone 1
shower has had notch cut in case at top and the cable surface mounted (loose) fed straight in the top
spur for gas boiler taken from the immersion tank radial
I was leaning towards a C3 for all of these, your input please.
and on a different job I have SWA feeding a RCCB which feeds some H07 flex, the swa is protected by a 60947-2 with the disconnection time of 0.4 giving a maz reading of 0.19. The readings at the rccb are within tolarance, but at the end of the H07 are not. As the H07 is protected by the RCCB do I need to worry?