Hi guys,

I'm testing a communal area of flats, just lighting circuits mainly and in the board they go to a timer and then off out to lights etc. And all lights are on push switches or pneumatic switches. But I can't get any insulation resistance reading. It's like 0.13meg

Is it the switches and the timers in the board bringing it down I'm guessing? And is there an easy way of getting a reading

Thanks
 
maybe just IR test with L/N shorted and test to E.
 
Have you disconnected the outoing cable from the board LN&CPC and carried out the IR tests?
 
Have you disconnected the outoing cable from the board LN&CPC and carried out the IR tests?

Haven't disconnected anything yet as the board is very congested and the terminals are tiny at the bottom of the timers. I was hoping there was maybe a work around. I guess I'll have to disconnect them and IR it
 
Haven't disconnected anything yet as the board is very congested and the terminals are tiny at the bottom of the timers. I was hoping there was maybe a work around. I guess I'll have to disconnect them and IR it
That would be my option
 
Haven't disconnected anything yet as the board is very congested and the terminals are tiny at the bottom of the timers. I was hoping there was maybe a work around. I guess I'll have to disconnect them and IR it
What voltage were you using with the timers etc still in circuit?
 
What voltage were you using with the timers etc still in circuit?

I've done it now and it's all good thanks. Just being lazy and was hoping there was an easier option lol.

500v, it's as low as the fluke tester I've been given to use will go. Only has 500v and 100v options
 
I've done it now and it's all good thanks. Just being lazy and was hoping there was an easier option lol.

500v, it's as low as the fluke tester I've been given to use will go. Only has 500v and 100v options
Are any of the electronics fried due to sticking 500v across them?
 

Reply to EICR flats communal areas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
788
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
835
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock