Just done an EICR on an outbuilding that is habitable (kitchen/wetroom etc). Supply is taken from henly block in the meter cupboard, via 2 core SWA to building. At building SWA is glanded into a metal box but the box (earth) is not connected to the plastic consumer unit which sits right next to the metal box. Ze for the outbuilding rod is 350ohms.

So I've got 2 problems, 2 earths (house PME) and outbuilding (TT) in close proximity and the TT giving a poor reading.

Water supply to outbuilding is in plastic pipe and in the outbuilding the connected copper pipework is bonded.

Whats stopping me using the SWA to provide the PME earth to the outbuilding, to fix both problems? I know the water pipes are bonded but they are not extraneous, although I haven't done the test to confirm.
 

Whats stopping me using the SWA to provide the PME earth to the outbuilding, to fix both problems? I know the water pipes are bonded but they are not extraneous, although I haven't done the test to confirm.

as long as there's no extraneous in the outbuilding. if there is after you've tested (if <22kOhms, then you'd need a 10mm bonding conductor from the house MET. alternative would be to improve the Ra of the TT system and ensure the outbuilding installation is RCD protected.
 
Why didn't you test from MET to pipe work? >22k ohms then not extraneous! But surely would be better to improve Ra , what electrode is in place sounds like a 3/8? Is there an up front RCD,?
 
Why didn't you test from MET to pipe work? >22k ohms then not extraneous! But surely would be better to improve Ra , what electrode is in place sounds like a 3/8? Is there an up front RCD,?

As in my first post wanted to try and kill 2 birds with one stone, re mixture of earthing in one location. Existing electrode is the thin one that you can't extent. 10 years ago Ze was about 150, also its on a side of a hill and I suspect will need a few rods knocked in to get a decent reading, so looking for an easier solution.

CU has 100mA time delayed RCD up front with 30mA for sockets.
 

Reply to EICR remedial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
611
What would of stopped this happening? Job I did this morning. SWA supply for outbuilding had sliced basic insulation at the gland due to poor...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock