Large commercial office
Installation circa 1996.
Asked to price up some work further to a PI being carried out.
I called in yesterday for a quick chat.
The EICR has multiple C1, 2 and 3 recorded but still satisfactory overall.
They have a 9.8 @ 240 (9.0 @ 230) shower in a ladies toilet wired in 6mm singles and protected by a 40a MCB that was given a C1 due to cables being melted at MCB terminal.
Live snipped and left floating.
Their Recommendation; rewire circuit with 10mm and change MCB to RCBO. 10m run
The single phase mc board supplying the circuit also had 4 SWAs glanded and bolted to its base.
There was no tags from the bolts to the earth bar.. Coded C2.
No RCD protection for sockets throughout building.. C1
Missing consumer blanks.. C2. Still missing.
I am going back next week to go through the report, should be interesting.