The R1+R2 and R2 column are all blank although it states one should be entered. No end to ends of ring final conductors, I would say that schedule is incomplete.
Discuss eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
That's for new installations. I'll bet during an EICR that the insulation resistance readings between live conductors won't be filled out. There is nothing wrong with "LIM" being inserted in any of those boxes - just agree it with the client beforehand.The R1+R2 and R2 column are all blank although it states one should be entered. No end to ends of ring final conductors, I would say that schedule is incomplete.
... My mate even showed me his tutors eicr which shows he doesn't carry it out saying only needed on new installs only not on eicr as its already energised
The top of the column clearly states one should be listed, not put NA in each box.That's for new installations. I'll bet during an EICR that the insulation resistance readings between live conductors won't be filled out. There is nothing wrong with "LIM" being inserted in any of those boxes - just agree it with the client beforehand.
I think Chris's Vid will answer your question
1983 may be a good idea to ask your mate to ask his Tutor what he thinks of the video.
Thank you everyone for the feed back I've always done the full test but after hearing this from my mates tutor who's teaching the 2395 and also showed me the tutors old eicr papers where all I see is n/a in the R1+R2 column got me thinking have I been wasiting time
The top of the column clearly states one should be listed, not put NA in each box.
Replies to date just go to show how this is interpreted. GN3 guide for me.
But I suspect that a considerable amount of testers don't do full dead tests as part of the eicr.
Just trying to show the OP the correct procedure for testing RFCThat is for testing a new install covered under 2394 not 2395 which is periodic there are diferent requierments, it is down to the tester what test needs to be carried out and agreed with the customer and clearly stated on the cert
You should at least do an end to end test and a figure of eight, this should give a rough indication of the Zs.
That fence they sit on must be well worn.Spoke to the nic he said no two places are the same it's about your feel on the installation if you find there as been alteration then do it if you feel it looks good readings good end to end then it's ok all bout your professional judgement I think I'll carry on doing it the way I have been all test that's involved just bit shocked what some colleges are teaching
Again I would point you to the guidance in Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made. Again, like I said, end-to-end tests on the circuit conductors would seem to be reasonable in these circumstances. Obviously the Zs of all socket outlets should also be verified.However, it doesn't prove any of the above. Only the 3-stage RFC testing procedure can, hence why we do it in the first place.