If you had a 15 kw cooker.I'm glad that even seasoned professionals are struggling to find agreement here.
I accept the argument that for the purposes of future proofing a new cooker circuit you would wire it in 6mm.
Is the radial in 4mm at 32 Amp something to do with greater potential diversity. However if you were doing a new installation then you would make design decisions based on anticipated current demand?
Just my novice interpretations.
15000/230 = 65 amps
Diversity first 10 amps plus 30% reminder.
So that's 65-10 is 55
30% of 55 is 16.5
16.5 + first 10 amps = 26.5 plus 5 amp with socket if any =31.5 amps applying diversity.
So choose a cable that has the ccc of at least 31.5 amps.
Subject to reference method,volt drop and any other derating factors.
If 4mm is acceptable then it's acceptable.