OP
antimatter
You clearly have not produced anything to prove a tncs earth can not be exported
Ans you haven't proved that it can.
Discuss Exporting the earth? in the Industrial Electrician Talk area at ElectriciansForums.net
You clearly have not produced anything to prove a tncs earth can not be exported
Ans you haven't proved that it can.
IQ and Lenny did. What more do you need?
Antimatter,
can I ask then, if you are installing outside lights or sockets wired to the main building which is on a TNCS....do you rod them individually,and separate the earth....or use the TNCS?....I ask because logically if you are so appalled by the thought of a shed on a TNCS then presumably you feel the same about an outside light?.....if not why not?
The best example is the outside socket, used exclusively in the main for garden tools and the like.... If there is a possibility of RISK, then surely this is the best example of how ludicrous some of these objections are!!!
Outside light has the CPC connected to the MET, if extraneous metalwork in an outbuilding can introduce an earth potential within the installation.
I think you are a wind-up, either that or you haven't bothered to read any of the posts that don't agree with your very confused version of the Reg's, ....or come to that ''common sense''
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
Straight from the IET FORUM
The inspector has asked for a metal shipping container cabin housing a db for a soil washer to be made into a TT as the supply is a TNCS pme .Now i understand you cant export PME but the feed for this db comes from another metal cabinet which in turn is fed from a metal shed all pme .
so is this user on the IET forum wrong as well chaps? or do you want me to post more examples?
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
If you bothered to read the rest of the thread that you copied & pasted that post from, you would see that they infact agree that PME can be exported to an outbuilding!!!!!!!!!
If you bothered to read the rest of the thread that you copied & pasted that post from, you would see that they infact agree that PME can be exported to an outbuilding!!!!!!!!!
I can no longer deal with this......in the words of Peter Jones......I'm out.
Reply to Exporting the earth? in the Industrial Electrician Talk area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.