Two part question: Existing 16mm tails are over 6m in length from meter. They are encased in 32mm steel conduit running through a concrete floor and vertically up a block wall right upto the consumer unit. There is no place to install a de-rated switch fuse for isolation or protection. Is it sufficient just to mention this as a comment on the certificate when carrying out a CU upgrade?
The replacement CU would need to be moved downstream a further 2m as the existing wall is to be demolished. What is the best way to extend the tails as the cables will need mechanical protection and the joint will be inaccessible afterwards?
 
Two part question: Existing 16mm tails are over 6m in length from meter. They are encased in 32mm steel conduit running through a concrete floor and vertically up a block wall right upto the consumer unit. There is no place to install a de-rated switch fuse for isolation or protection. Is it sufficient just to mention this as a comment on the certificate when carrying out a CU upgrade?
The replacement CU would need to be moved downstream a further 2m as the existing wall is to be demolished. What is the best way to extend the tails as the cables will need mechanical protection and the joint will be inaccessible afterwards?


You need to come up with a way of installing a new cable and a switch fuse IMO and don't say you can't as there is always a way but might involve more cost/time. Ain't any one else's problem if you haven't thought about this situation and priced the job wrong and now have dropped a clanger.
 
Last edited:
Is that the rating if the fuse inside the carrier, or what it says on the carrier?
 
Two part question: Existing 16mm tails are over 6m in length from meter. They are encased in 32mm steel conduit running through a concrete floor and vertically up a block wall right upto the consumer unit. There is no place to install a de-rated switch fuse for isolation or protection. Is it sufficient just to mention this as a comment on the certificate when carrying out a CU upgrade?
The replacement CU would need to be moved downstream a further 2m as the existing wall is to be demolished. What is the best way to extend the tails as the cables will need mechanical protection and the joint will be inaccessible afterwards?


Sounds like you'll need to find another route to the repositioned new CU and abandon the 32mm existing containment unless you can extend the floor chase to the new position. At least with a new cable and route you'll be able to find space for a switch fuse. Next thing you need to decide is what type of cable you are going to use to supply the repositioned CU....

I wouldn't be thinking about jointing single tails to be honest. If you intend extending the metal containment use one of the cables as a draw line to pull in new tails. You might have to pull the cables into the extended sections bit by bit as you are installing, if there are too many bends. Not a very good practice at the best of times, and no chance of ever being able to rewire in the future!!
 

Reply to Extending Meter Tails in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock