SE48B250 KQ16 TP WAY 250 type B DISTwhat 250A D.B. have you been provided with ?
THX
Discuss Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net
SE48B250 KQ16 TP WAY 250 type B DISTwhat 250A D.B. have you been provided with ?
Must be a loose connection if the busbar is buzzingI'm working in a warehouse and replacing the old fuse boards with a new 3 phase board.
The board will be sitting directly above the buzz bar im not sure if I need to put in an isolator in between them to isolate the 3 phase board?
Thx
lolMust be a loose connection if the busbar is buzzing
WhyYou are not going to be able to do that.
Boss has told me to use 35mm tails into isolator then 35 mm tails to feed the dist board and to use the 125amp switch disconnector.Main switches for those boards are 125A, 160A, 200A or 250A and none offer circuit protection they are 60947-3 switch disconnectors. Off hand I am not certain if you can get a 60947-2 which offers circuit protection, if you can it will be the higher rated devices and not 125A.
My boss is telling me the dist- board needs an isolator before it incase someone wants to work on the board they don't need to kill the busbarBoss has told me to use 35mm tails into isolator then 35 mm tails to feed the dist board and to use the 125amp switch disconnector.
Does this isolator incorporate fuses.My boss is telling me the dist- board needs an isolator before it incase someone wants to work on the board they don't need to kill the busbar
No.its a CED SD 100Does this isolator incorporate fuses.
The expansion kit is fully insulated and allows for total isolation and access to the circuits without risk, you won't be even taking the lower cover off where the tails connect, I really haven't got a clue where he gets his ideas from but switching the main switch on most boards is often acceptible before removing the cover even though the tails remain live, you should know been domestic, when was the last time you removed a service fuse so you could open the consumer unit up?..Sounds like you have made (with our help) a very good suggestion and he is trying to justify poor design and wasted costs to save face by saying without any regularity backup that the dist board need external isolation after the busbar.My boss is telling me the dist- board needs an isolator before it incase someone wants to work on the board they don't need to kill the busbar
Not sure it does that part no comes up as a switch disconnector, a switch fuse disconnector is CED SF100. Look inside and post a pic.
View attachment 35552[
So could I just use this switch with no 100amp isolator or do I have to use an mccb thx