Discuss Floating SWA house to garage in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Reaction score
40
Been asked to add some sockets in a garage, the garage is supplied by a 2.5mm SWA which is Clipped up the wall of the house then crosses into the garage, about 800mm width and about 2.5meters up in the air.

Is this permitted? I can't see another way of supporting the cable.
 
could it not be re-routed. out of house low level, buried for the 800mm then into garage?
 
Hi,
Not only does most cable manufacturers not permit it to be used in thease instances.
SWA doesn't have any rating to be hung/suspended in the air, due to the nature of the the cores inside being of a Class 2 quality?
Only reason I've been pulled before with NICEIC
Hope it helps.
 
OP is in london. they got to have some aerial cable to hang their washing in those dog kennels they call houses.
 
Hi,
Not only does most cable manufacturers not permit it to be used in thease instances.
SWA doesn't have any rating to be hung/suspended in the air, due to the nature of the the cores inside being of a Class 2 quality?
Only reason I've been pulled before with NICEIC
Hope it helps.

Being suspended, and supported adequately by a catenary wire would prevent it from flexing ..... After all it's only 800 mm.

So as is, as described by the op, it would be prone to movement.... So by providing support you would be making the install better.

Just saying
 
I see what you are saying but reading what the manufacturer of a the bS number that cable is related to says it's made for "fixed" wiring.
But in true fashion it also then puts it back to designer.
Tbh when the new regs come out with Arc protection you will be covered anyway.
The reason I'm against it is my NICEIC assessor said it wasn't allowed.
800mm don't sound alot compared to my 1.5m when I installed it in the same method.
interesting still as I would of liked to leave it.
 
spin's strut is heavy duty galvanising. and it's all inch and 1/2". :)
 

Reply to Floating SWA house to garage in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
699
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
423
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
797
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock