Discuss Fluke testing problems in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
Hi, need some advice on testing with the fluke 1652c as had a few people show me different ways on how to do Ze at origin, PFC and PSCC
Ze at origin 3 lead test with main earth disconnected to remove parallel path, fluke set to no trip, then between incoming live, neutral and earth
PFC reconnected main earth then 2 lead between live and earth or 3 lead then test between live, neutral and earth then you press one of the functions to reveal KA or work it out from amps that come up ie 777A will be 0.78 KA rounded up
PSCC with earth connect back aswell either 3 lead or 2 lead between live, neutral seen some people do 2 lead and some people 3 lead with earth and neutral on neutral terminal and live on live
Thanks
 

Reply to Fluke testing problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi gents and ladies, I’ve just bought a Kewtech KT63, the instructions aren’t very clear on lead setup. When doing a Ze is this a 3 lead test on...
Replies
3
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
639

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock