Call out to a job,flat with Db protected by 30ma trip as main switch.
Rcd had tripped but not in clients flat,main intake area downstairs.
There I found a 30ma rcd which supplied Db in upstairs flat.
Apparently this as been tripping on a regular basis,& got worst,obviously no discrimination between rcd s,& so,a nuisance.
Did all the correct testing,& installation proved ok,rcd tripping times ok too.
Major concern is that it's a tt system,& there are other rcds in situ,controlling various other supplies.
At main intake a 100 ma time delay rcd is installed,& sometimes this trips,& causes havoc to all.
The flat seems to cause all this once tripped,tried explaining to client the ins & outs,but goes way over the head.
I think I gonna do a runner.