Hello

I have a question , when looking at a cartridge fuse that say's , 32A (32SB3) , and at the side it says 550V AC 80kA ( BS88.2 ) , can this be used as a 32A on 240V supply ! .

SpotBot
 
Last edited by a moderator:
Hi SpotBot, welcome to the forum, I have dropped your link out to the DIY forum on your same post you made there as it gave no more info than the question you have asked here.

There is not a straight forward Yes or No answer here as your circuit design and your Zs readings play a part into what device you use as overcurrent protection, so in reply to your question then as long as you meet the disconnection times and your fusing is within your circuits limits then your front end device can be various kinds of over current protective devices.
 
Hi - if you have more info we may be able to be more specific :)
 
I think the fundamental answer is yes it is suitable for use on a 230v supply.
 

Reply to Fuse rating in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
428
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Hello - I'm looking to help determine how many connections are allowed on my AC disconnect terminal lugs - Eaton DPU22R. I'm not seeing anything...
Replies
0
Views
425
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Hi there. I have noticed that most laptop power supply cables have a 5A fuse in the plug, but a 2.5A rating on the clover leaf end of the cable...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock