Discuss Fused spur from ring final for exterior lighting in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
57
Trying to calculate the voltage drop for a run on external lights supplied via 5Amp Fused/rcd spur from local ring final circuit. for a quotation and have got a bit confused re Voltage drop.

27m run in 1.5mm cable total load on lighting radial 420w. (no diversity as all lights either on or off)

(VD = Lx1.82x29/1000)

(Calculated Volt drop = 1.42 V)

estimated existing ring final circuit 60m long.( 30Amp 3036 fuse ) (VD= Lx26x18/1000/4)

Calculated Volt drop = 7 Volts)

Total Volt Drop origin to last light = 7.42V

For lighting circuits <3% 6.9V from origin to the last light

it appears the volt drop on the existing ring main will already be above the 3% or am i missing something, as it is standard practice to use a fused spur from a ring final to supply a security light.

any advice welcome
 
but how often will you see 26A on that RFC? i'd let it go.
 
If it’s a row of lights there is also cumulative volt drop to take in to account.

Cumulativevoltdrop_zps80e5393c.jpg
 
it appears the volt drop if spurred from the ring final is too high. Just calculated ZS and that is over the allowed Max for the 30Amp 3036 Ring main protective device, even though there would be a 5amp cartridge fuse in the rcd/fcu.

this is becoming messy, A new circuit from C.U is the answer i feel
 
it's a debateable issue with Zs values on a spur. one camp says use the RFC OCPD, and the other says use the 5A FCU fuse to establish max. Zs.

IMO, if you get a fault of negligible impedance on the spur, then the 5A fuse is the one that will blow within the specified time , so as long as the Zs for the spur complies with the max. for the 5A 1362, then that's OK for me.
 
it's a debateable issue with Zs values on a spur. one camp says use the RFC OCPD, and the other says use the 5A FCU fuse to establish max. Zs.

IMO, if you get a fault of negligible impedance on the spur, then the 5A fuse is the one that will blow within the specified time , so as long as the Zs for the spur complies with the max. for the 5A 1362, then that's OK for me.

This is the common sense answer!
 

Reply to Fused spur from ring final for exterior lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
657
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock