Michael, you have missed some essential points.
1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.
2. A time delay RCD (or any RCD) is NOT necessary at the house end.
1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.
2. A time delay RCD (or any RCD) is NOT necessary at the house end.