Discuss Garage earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Last plumber

-
Arms
Reaction score
176
Good afternoon, I'm new here, as some know, I'm from the other side, ( plumbers forum ).
I've had a couple of different opinions on this from three very experienced electrical engineers.
I've read regs but curious on whether you agree and what you think is safest way of doing this or how you would do it if it were your own property.

Supply to garage runs from RCBO in house consumer unit through the house in twin and earth.
Supply is PME.
It changes to SWA before exiting the house and runs 20 meters up the garden to the garage.
The garage has a steel door.
The question is, is it safer to use the earthing from the SWA ( house earth) or is it safer to use an earth rod and separate earthing system.
 
Does your garage have any other services, gas, water etc? if so you need to consider a bonding conductor as well
 
Any extraneous metal in the garage?

Perfectly fine using the armor as the earth if not.

Earth rod will not do any harm, but getting a resistance low enough (Ra) to be useful isn't particularly easy.
 
It is safer to use the PME earth. The problem is if there are extraneous conductive parts in the garage (water or gas services usually) they require bonding back to the met with a 10mm csa or equivalent armourings may comply depending on cable size .
The steel door is not usually extraneous.
 
I did wonder about the door, if it's not classed as extraneous that's fine. Thank you.

There are no other extraneous parts at the moment.
I think in future ( and this is part of the five year plan as my mrs calls it, sarcastically), there may be a storage tank ( rainwater) with a pump housed inside the garage and an outside tap.

To be honest I was going to use the earth supplied from house. In my mind it was the safest way. It is supplied from an RCBO too so I didn't contemplate another way until a commercial spark said it was a no no !
 
If you want to future proof your garage you could always add the following along with the power cable.

Ethernet cable.
Alarm cable.
Phone cable.
TV signal cable.
 
In your situation I too would go with the PME earthing . If you have to add a tank etc , do as Mykey says and use plastic. A nice sturdy narrow oil tank would suffice for that. The rest of non conductive plumbing stuff you will be well aware of.
As a matter of interest what were you recommended to do . Keep it clean ;)
 
FYI , all of you !
I don't use plastic unless it's absolutely necessar. That's because it's crud !

You've all been very helpful, thank you. I knew however, that it would turn to this, pathetic immature behaviour !

There's enough on the other side. I thought over here I'd find intellectual conversation, alas ''twas not to be
 
Lol , I know what you mean about plastic, but you could relent on this occasion.
are you not going to tell us what you were advised regarding earthing? :)
 
In your situation I too would go with the PME earthing . If you have to add a tank etc , do as Mykey says and use plastic. A nice sturdy narrow oil tank would suffice for that. The rest of non conductive plumbing stuff you will be well aware of.
As a matter of interest what were you recommended to do . Keep it clean ;)

I was recommended to:-
Terminate the SWA in a box ( plastic)
Continue through into another box with just L + N
Install an earth rod
Connect all earths in garage to that rod
Test the earth resistance through the ground.

I see the aim but I didn't think it was as safe as how I was going to do it

I know if you lost your incoming neutral you in effect have lost earth too in theory but how likely is that ?
Is it not more likely that your earth rod will be a poorer earth during the devastatingly long hot summers of Lancashire ?
 
Yes unlikely but possible.
If it did happen you could hope that what was left of the pme neutral bond to earth is still better that your rod.

24900-9fb8cb8ae9ef867e4c59c438780cb367.jpg


pme-explanation-uk2.gif

pme-explanation-uk2.gif

I know that went haywire , but I could not get rid of them.
 
I'd run the SWA as 3 core with it's own earth core as well as the SWA steel earthed. I can't see a local earth rod would be a problem and adds an extra bit of protection but the chance of a lose of your earth is very slim.
 
What CSA is the SWA you've run? Just curious what volt drop you may get.
 
Last edited:
I was recommended to:-
Terminate the SWA in a box ( plastic)
Continue through into another box with just L + N
Install an earth rod
Connect all earths in garage to that rod
Test the earth resistance through the ground.

I see the aim but I didn't think it was as safe as how I was going to do it

I know if you lost your incoming neutral you in effect have lost earth too in theory but how likely is that ?
Is it not more likely that your earth rod will be a poorer earth during the devastatingly long hot summers of Lancashire ?

What part of Lancashire are you talking about, all it does where I live is bloody rain!
 

Reply to Garage earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
396
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock