Discuss Garage Supply - 2 way metal consumer unit in a seperate garage in the UK Electrical Forum area at ElectriciansForums.net

time delayed rcd in the house protecting the garage circuit, that way the rcd in the garage consumer unit will trip first.

The op has already said the cu is a dual RCD unit with no spare ways - how is adding a time delay going to improve the situation? And why do people think by TTing a shed or garage would prevent the house cu RCD tripping?
 
Replace one rcd with the delay one? OP wants to avoid the garage potentially tripping an rcd in the house, so if there's a short in the garage the garage cons unit should trip before the house one if it's a timer delay one. On a 5m run it's not that big a deal to have to flick a switch in the house c.u. We recently did a farm shed that was about 120m from the main supply and that's what we did - time delayed rcd in house c.u. and normal rcd in the shed. 16mm cable to run the power to the shed because of the length of run with voltage drop.
 
Shame it's not a high integrity dual rcd board, I just installed a similar set-up, but used an mcb to protect the 4mm swa for the garage which had a 63A RCD main switch with 2 mcbs in the unit.
Never been a fan of large consumer units with no none RCD ways.
 
Replace one rcd with the delay one? OP wants to avoid the garage potentially tripping an rcd in the house, so if there's a short in the garage the garage cons unit should trip before the house one if it's a timer delay one. On a 5m run it's not that big a deal to have to flick a switch in the house c.u. We recently did a farm shed that was about 120m from the main supply and that's what we did - time delayed rcd in house c.u. and normal rcd in the shed. 16mm cable to run the power to the shed because of the length of run with voltage drop.
Because it would make the other existing circuits non compliant
 
The only thing that's not been mentioned and I'm sure someone will correct me, I was told by an ELECSA assesor that you're not allowed to export a TNCS earth in less than 10mm cable. So, as you can't get an mcb unprotected in the house consumer unit, have a main switch in your garage consumer unit and put an earth rod in to earth your garage consumer unit.
 
The only thing that's not been mentioned and I'm sure someone will correct me, I was told by an ELECSA assesor that you're not allowed to export a TNCS earth in less than 10mm cable. So, as you can't get an mcb unprotected in the house consumer unit, have a main switch in your garage consumer unit and put an earth rod in to earth your garage consumer unit.

Here goes then; in a typical domestic property, the 10mm bit only relates to the minimum size cable if you have extraneous conductive parts to bond. Or run a separate 10mm protective bonding conductor to the extraneous conductive part in the garage, and run an appropriate sized swa for load/vd only. Or as you suggested turn supply into TT, bonding locally as necessary.

Don't think there is an extraneous conductive part in the situation described by the OP.
 

Reply to Garage Supply - 2 way metal consumer unit in a seperate garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
691
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
20
Views
4K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
692
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock