Discuss Generator earth electrod? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I wire out mobile decontamination units that have a 3 kva generator.

We supple earth electrodes with our units for use with the generator.
Every circuit is protected by an 30ma rcd and the generators earth and neutral are conected in the generator.

Because the generator is under 5 kva, rcd protected and earth neutral linked is an earth electrode needed?
 
If there is a socket outlet anywhere, then yes, so that the ADS still protects a user who runs an extension lead outside the equipotential zone of the unit. If not, then, hmm....
 
The biggest problem we had with the larger gennys in the hot and dusty places was getting them to go on line when they self check the earthing, the ground was too dry and it took a lot of water to get them going...
 

Reply to Generator earth electrod? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
505
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
398
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
713
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
977

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock