Hi all, first post for some time! Currently installing power and lighting into a small cabin. Supply will be from a permanently connected generator and using a rod for earthing purposes. Carrying out testing today and only getting 197v between live and rod. Guessing I may need another rod which I didn't have with me but there was a couple of old steel beams concreted into the ground so I connected to them to see if it would help but no diffence. Is installing a few more rods going to help, if not I don't know what else to do!
 
Hey SS - perhaps check one pole of the gen output is solidly connected to your earth rod, as it might be floating ?
 
Last edited:
Sounds like gen has an isolating transformer type output and might be intended to power a double insulated power tool? Gen details? (I can try to look it up on line)
 
Yes sounds like generator output is floating so you have an IT system not TN. You will need to investigate the N-E link options if you want TN.
 
There is no definitive answer. There are pros and cons for separated systems, although the larger the installation and the greater likelihood of undetected first earth faults the greater the argument in favour of earthed TN-S. BS7430 might have some useful info, see also points 11 & 12 here: OC 482/2: Electrical safety of independent low-voltage ac - http://www.hse.gov.uk/foi/internalops/ocs/400-499/oc482_2.htm

As to where to make an N-E link, maybe in the genny terminal box, maybe at the CU, the genny maker might have made specific provisions.

Don't forget that when you are testing the rod, it's not like an earth rod on TT where you're picking up an earth from the supplier's substation via the ground. Here you are the supplier and you are referencing your system to it.
 

Reply to Generator earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
505
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
969
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K
Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock