S
Sandman34
Hi all new to the forum and electrican. Working on a plant at the moment where the client is wanting to have two 480volt 60hz three phases motors installed inside there workshop. These motors are going to be fed from a generator as they do not have enough power to feed them off the workshop supply. So generator provided and a distribution board installed inside the workshop for isolation and protective devices for the two motors. The supply at the workshop is 415volt 50hz three phase and neutral. Now just have a few questions before I start.
1. I would like to run the motors at there nameplate rating so would set the generator up to supply 480volts 60hz. Will this be ok considering that the workshop supply is 415volts 50hz?
2. The generator will be sited outside the workshop and for earthing I am looking to do as follows. On the generator main switch generator side neutral connection has an Earth cable from there to the frame of the generator. I was planning on taking a Earth from this point half the size or more of the phase conductor to the distribution board sited inside the workshop then from the distribution continue the earth to the M.E.T of the workshop this will get the neutral grounded and also having a Earth at my distribution board. Then there are Earth bosses either side of the generator in the lifting frame which the lifting frame is bolted to the the generator frame. So I am going to take half the size or more of the phase conductor from one of the earth bosses to the M.E.T inside the workshop. Will this set up be satisfactory?
3. Setting of the MCCB of the generator. Generator has a 630amp MCCB. I am only needing to run 185mm cables from the generator. So settings of MCCB is as follows
- Io= In * 0.5 = 315amps rating is the breaker now
Ir= Io * 0.8 = 252amps trip point
Isd= Ir * 8 = 2016amps for starting inrush current
Motors are both 55kw. Is this set up correctly.
4. Generator has a RCD inside the generator. I am not taking a neutral out of the generator as motors do not require it my RCD at 30ma will still work as have link between Earth and neutral that is inside the generator connection from neutral gen side the the frame of the generator.
5. As limited Earth connections for on the distribution board that I have supplied with the cable I am installing planning on having the Earth cable from generator onto the earth boss inside the dist board. Then linking 0.5 or more of the phase conductor from that Earth boss to another Earth boss on the distribution board which is an Earth bolt then from there taking 0.5 or more of the phase conductor from outside the enclosure onto this same bolt to the M.E.T of the workshop. Is this satisfactory?
Is this set up all satisfactory? Sorry for the long message be much appreciated if can answer my questions.
Kind regard
1. I would like to run the motors at there nameplate rating so would set the generator up to supply 480volts 60hz. Will this be ok considering that the workshop supply is 415volts 50hz?
2. The generator will be sited outside the workshop and for earthing I am looking to do as follows. On the generator main switch generator side neutral connection has an Earth cable from there to the frame of the generator. I was planning on taking a Earth from this point half the size or more of the phase conductor to the distribution board sited inside the workshop then from the distribution continue the earth to the M.E.T of the workshop this will get the neutral grounded and also having a Earth at my distribution board. Then there are Earth bosses either side of the generator in the lifting frame which the lifting frame is bolted to the the generator frame. So I am going to take half the size or more of the phase conductor from one of the earth bosses to the M.E.T inside the workshop. Will this set up be satisfactory?
3. Setting of the MCCB of the generator. Generator has a 630amp MCCB. I am only needing to run 185mm cables from the generator. So settings of MCCB is as follows
- Io= In * 0.5 = 315amps rating is the breaker now
Ir= Io * 0.8 = 252amps trip point
Isd= Ir * 8 = 2016amps for starting inrush current
Motors are both 55kw. Is this set up correctly.
4. Generator has a RCD inside the generator. I am not taking a neutral out of the generator as motors do not require it my RCD at 30ma will still work as have link between Earth and neutral that is inside the generator connection from neutral gen side the the frame of the generator.
5. As limited Earth connections for on the distribution board that I have supplied with the cable I am installing planning on having the Earth cable from generator onto the earth boss inside the dist board. Then linking 0.5 or more of the phase conductor from that Earth boss to another Earth boss on the distribution board which is an Earth bolt then from there taking 0.5 or more of the phase conductor from outside the enclosure onto this same bolt to the M.E.T of the workshop. Is this satisfactory?
Is this set up all satisfactory? Sorry for the long message be much appreciated if can answer my questions.
Kind regard