- Reaction score
- 10,224
The only info I have on the jaixipera compressors is a cross reference chart that shows the max start current as 10.6A (230v @ 50Hz) which is pretty close to what Defy told you so I'd probably work on an 11A maximum requirement from your generator at 240v. I think the 2.2KVA unit may be a little shy of the mark, as Lucien says it will depend very much on the electronics in the generator's AVR. If you can try before you buy then I'd start with the 2200VA or 2500VA Honda, if not and you want to guarantee it will work I'd go with a 3000VA Honda which will give you 12.5A Max, that way there's a small allowance for power factor there as well.
*Edit* I personally wouldn't recommend you run a 50Hz compressor on 60Hz, it will affect the head pressure the compressor is under, the system may also under condense especially in high ambient temperatures in Zambia and could result in refrigeration problems and maybe even premature compressor failure. Domestic refrigeration on R600 can be a bit skittish and sensitive at the best of times. I'd suggest you stick with a 230-240v 50hz genny which should be the local standard.
*Edit* I personally wouldn't recommend you run a 50Hz compressor on 60Hz, it will affect the head pressure the compressor is under, the system may also under condense especially in high ambient temperatures in Zambia and could result in refrigeration problems and maybe even premature compressor failure. Domestic refrigeration on R600 can be a bit skittish and sensitive at the best of times. I'd suggest you stick with a 230-240v 50hz genny which should be the local standard.
Last edited: