Deleted member 9648

Currently doing an EICR and would like some advise on loadings on an air to water heat pump as my experience of these is limited.
The pump is a single phase Mitsubishi PUHZ-HW140VHA and the rating plate states 'rated current 23.3/14.9a' and 'maximum current 35a'.
The unit was recently installed and is fed from an existing 10.0mm 40a supply extended in 4.0mm (joined with 15a(!!) connectors in a wiska box) to a 32a rotary isolator externally.
Now I'm thinking that if the 'maximum rated current of 35a' applies then both the 4.0mm and 32a isolator are inadequate, but as this will likely be thrown back at the original installer I'd like to be sure before coding.
Thanks in advance for any advise.
 
Currently doing an EICR and would like some advise on loadings on an air to water heat pump as my experience of these is limited.
The pump is a single phase Mitsubishi PUHZ-HW140VHA and the rating plate states 'rated current 23.3/14.9a' and 'maximum current 35a'.
The unit was recently installed and is fed from an existing 10.0mm 40a supply extended in 4.0mm (joined with 15a(!!) connectors in a wiska box) to a 32a rotary isolator externally.
Now I'm thinking that if the 'maximum rated current of 35a' applies then both the 4.0mm and 32a isolator are inadequate, but as this will likely be thrown back at the original installer I'd like to be sure before coding.
Thanks in advance for any advise.

Hi, well the simple way to look at is the manufacturer stipulates a 40 Amp MCB, so unless we are omitting overload,which in this case we shouldn't be, then we need to meet IZ>IN>IB.

So i agree it should be coded appropriately.
 

Reply to Heat pump advise please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
Hello. I was hoping someone could please help me with some queries? I’ve just taken delivery of a single phase pool heat pump rated 1kw, with...
Replies
7
Views
2K
Is it a requirement to provide overload protection to a central heating pump rated at 2.77amps? I’m kinda under impression that an almost 3 amp...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock