Discuss Help 3phase dishwasher in the Electrical Appliances Forum area at ElectriciansForums.net

B

brum

Hi guys fitted a commercial dishwasher today extended c/w supply made drainage alterations etc.Being a helpful stupid bloke connected up cables.Didnt know neutral changed from black to blue so have connected up incorrectly none of the breakers tripped am I in the brown stuff or not im a plumber to trade(thought it better to put that in last)In my day blue was a phase and black neutral...help plz:willy_nilly:
 
Hi guys fitted a commercial dishwasher today extended c/w supply made drainage alterations etc.Being a helpful stupid bloke connected up cables.Didnt know neutral changed from black to blue so have connected up incorrectly none of the breakers tripped am I in the brown stuff or not im a plumber to trade(thought it better to put that in last)In my day blue was a phase and black neutral...help plz:willy_nilly:

if it's 3 phase what were the other colours of the live phases and neutral, red yellow blue and black or brown black grey and blue? if it's the latter then go back and change it before it is turned on
 
Hi,

If I was you I would slip an Electrician a nice wedge to come and have a look for you, or alternatively ask some nice ladies ( no inference intended to the opposite sex here, but they are so much better at this than us lowly gentlefolk) to do the washing up.
Strap yourself in tight , it's going to be a rough ride.

Regards.
 
3 phase dishwasher... is that 3 diffeernt birds on shiftwork in my kitchen..... heaven.
 
Hi guys fitted a commercial dishwasher today extended c/w supply made drainage alterations etc.Being a helpful stupid bloke connected up cables.Didnt know neutral changed from black to blue so have connected up incorrectly none of the breakers tripped am I in the brown stuff or not im a plumber to trade(thought it better to put that in last)In my day blue was a phase and black neutral...help plz:willy_nilly:
Yes, "harmonised" colours have been around for a few years now.
I think the idea was and is madness.
For the very reason you have illustrated. Confusion.

That doesn't absolve you from the gaffe. It's a job you should not have undertaken.
But I do have sympathy - you were trying to help.

I don't know what the consequences are likely to be in terms of possible equipment damage.
You've swapped a phase and the neutral. Some bits of the kit will get line to line voltage as they should. Other things like motors expecting 3-phase will get unbalanced.

But possibly worst is that some bits of the kit designed for line to neutral will get line to line voltage. Not good. Possible or even probable damage.

I'm sorry I can't be the bearer of better tidings........
 
Yes, "harmonised" colours have been around for a few years now.
I think the idea was and is madness.
For the very reason you have illustrated. Confusion.

That doesn't absolve you from the gaffe. It's a job you should not have undertaken.
But I do have sympathy - you were trying to help.

I don't know what the consequences are likely to be in terms of possible equipment damage.
You've swapped a phase and the neutral. Some bits of the kit will get line to line voltage as they should. Other things like motors expecting 3-phase will get unbalanced.

But possibly worst is that some bits of the kit designed for line to neutral will get line to line voltage. Not good. Possible or even probable damage.

I'm sorry I can't be the bearer of better tidings........

can't agree more. absolute lunacy. harmonisation with what? the french, no they still cling to red,white,blue, as it's the flag of the king killers. spanish. no, they use whatever colour suits. germans, who cares, we won.
 
Bit late now but for future you need to manually check what colour they've used for neutral when connecting up any 3-phase appliance.

The components most likely damaged by incorrect wiring are the control board and any other electronics there may be plus the motor. You (or someone more knowledgeable with electrics) needs to test all the components and repair/replace them as necessary.
 
Well thanks guys I was expecting a lot more abuse sparky came over and changed black and blue connections fired it up and away it went.A very valuable lesson has been learnt this weekend tonight I will sleep need to make up for last nights lack of.Thanks again
 
wish they would have told me
Incumbent upon you to find out before playing around with wiring.

I don't mean that unkindly but what you did could have caused damage and possibly put others at risk.

A positive outcome is that you have, inadvertently or otherwise, highlighted the issue.
No doubt you will have learned from it. Perhaps others can too.
 
This is a little lesson in testing to prove what is,and not what should be. I have come across items of equipment connected incorrectly,that functioned fine,because the 3P N+E was wired incorrectly upstream,on a different occasion. A case of two wrongs maybe not making a right,but possibly saving a life...colours,markers,labels,they all remind me of what my dad used to say when he was teaching me to drive..."See that car with its' nearside indicator on,son?...all that tells you for sure,is the lamps working..." :bow:
 

Reply to Help 3phase dishwasher in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm trying to rewire an old plug. I've rewired a few in my time, but all have been with the post-2006 wire colours. I have this old welder...
Replies
3
Views
827
hi need help with wiring this. basically new build with combi boiler, unvented cylinder with dual channel hive ive attached pics with the wiring...
Replies
39
Views
6K
Hi, im having trouble. I want to wire up some outdoor lights through a smart home plug. They were previously connected to an analouge timer and...
Replies
4
Views
1K
Hi all, Having trouble wiring up a two zoned wet underfloor heating system which is part of a manifold and controlled by one 4 wire actuator. Ive...
Replies
6
Views
2K
Morning fellow practicioners of the dark art we call ELEKTRICKARY , I have recently been ask by a close freind if i thought his electric bill...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock