Hi guys

Need a bit of help on testing in a hotel (bit of background) its a 7 storey building with main switch room in basement as a working hotel nothing can be switched off. On the 7th floor existing rooms were refurbished with 8 new rooms added
there is a busbar trunking running up the hotel from switch room and a tap off on every floor
on each floor a 3phase board numbered (db15) which supplies power to each room then in every room there is a fuse box for all in rooms
Now i have to test all of this so testing the fuse board db15 feed to each rooms thats ok and testing of rooms ok
but testing the busbar or main switch room for my main readings for the KA, ZE, and all info for particulars of installation at origin nothing can be switched off also this hotel has no previous test info as was bought over a few years ago and no info was left
id be grateful if you could give any advice on this test procedure
could i put the 3 phase board down as the origin thats on 7th floor if i cannot get this info, would the 3 phase tap off be my main switch which is 3 x 60amp fuses which feeds the 3 phase board

thanks again guys
 
Your origin of supply is always the incoming head from the DNO.

If you are just testing DB15, then just fill out the test sheet as needed, the put any values from the origin as either N/V or you could enquire for them? You can still test your PFC and PSCC at origin just your Ze will be not possible to be measured. Note anything not possible on the relevant section of the EICR.
 
Your origin of supply is always the incoming head from the DNO.

If you are just testing DB15, then just fill out the test sheet as needed, the put any values from the origin as either N/V or you could enquire for them? You can still test your PFC and PSCC at origin just your Ze will be not possible to be measured. Note anything not possible on the relevant section of the EICR.


dill would i not need a EIC not a eicr as some rooms are new sand refurbed rooms rewired
 
Sorry thought you were carrying a a EICR my bad.

Yes EIC for new circuits and a MWC for any circuits that have been altered. But all the other info still stands, really it's just a Ze you won't be able to obtain so enquire to the DNO for that value.
 
As you can't switch anything off, i would be very specific on the paperwork, and make sure it is very clear in the extent and limitation box what you have and haven't done, and for the stuff you haven't done, be clear as to the reasons why, as with all theses things it is your bum on the chopping block, and when the insurers or whoever decide to want to see the paperwork at sometime in the future, you don't want be carrying the can for things you couldn't do, so make sir sit is well covered. I personally can't see the benefit of having an EICR done, if you can't at least check the Zs results for all the final circuits, especially in rooms for use by the public. If your Zs's are Ok then in all probability everything else will be OK with the exception of ring continuity which you can't do live and you can't find problems with unless dead anyway. If there are low IR readings etc, then they will have to live with it, and when they get low enough they will start getting faults anyway.

Cheers...........Howard
 
Is this the EICR you mentioned a while back on here mate, vaguely remembering you posting regarding a job or something. If this is an EIC, test everything. If its an EICR, what was the agreement between you and the customer?

If you responsible for the initial verification of these new refurbed rooms, then yes, you will need an EIC for these rooms alone. It also will need the signatures of the designer and the constructor.

Your origin of the supply will be the incoming service head/service head belonging to NIE in this case.

To be honest mate, if there is no scope for testing and switching things off, then this EICR sounds like a LIM-a-thon. Make sure you stick a limitation down against everything you didn't and can't do.
 

Reply to help with testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
780
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
240
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock