Strange one today that i've never seen before - hoping someone else may have seen this...
Wiring an additional outside bulkhead today - couldn't easily get to the last fitting to take a switch wire from there so split the switch wire as close as i could to the fitting and wired in a junction box. Took a spur from the junction box as well as connecting up the other light.
Anyway, came to do the testing and was getting 48 ohms on my R1+R2?? Strange thing is that the loop impedance is fine (1.14 ohms) and the RCD is OK too. There was already an RCD on the circuit before hand.
Has anyone experienced this before? Surely if there was anything untoward then you would expect the earth loop imp to be high?? Im starting to wonder if my tester is playing tricks.
Thanks