Hi, I was wondering if you guys can help with some errant test results.

I'm testing a ring and i get
L-L = 0.41
N-N = 0.40
E-E = 0.63

Great

Figure 8 L-E = 1.0 ohms.

Still good

Figure 8 at each socket varies from 0.8 ohms to 1.1 ohms (I was expecting much lower)>

Oddly Zs = 0.23 (which is what I was expecting for both this and my R1-R2 [at socket] tests.

Any ideas?? System is TNS / Ze of 0.09

Maudy
 
your fig.8 R1+R2 should approximate (r1+r2)/4 so your 1.0 ohms looks high. are you sure you have nulled leads for the R1+R2 readings?
 
check at terminals of outlets as i installed a load of mk sockets and readings at fron varied wildly
N terminals were hard work to screw down plastic seemed to be restricting it

ended up removing them all and replacing with BG

also as you say your reading increased was this to the mid point of the ring as you could have incorrectly identified the legs and not carried out cross connection correctly
your R1 +RN should be more like 0.2 and your R1 +R2 should be around 0.26ohms or within 0.05 ohms of each other so 1.0ohms to high
 
How are you measuring your figure of eight? It sounds asthough you are disconnecting the cables from the sockets and measuring 2 end to ends as the results are your L-l and E-E added together
 
How are you measuring your figure of eight? It sounds asthough you are disconnecting the cables from the sockets and measuring 2 end to ends as the results are your L-l and E-E added together

Mhahaha

Yea - its wired in T&E so I wouldn't make that mistake.

It not that the socket readings start off low and get higher - they're all too high. Or as I suspect the figure 8 end to end (measured at the board) is too low. WHich makes me think Murdoch is right.
 
How old are your tester leads?


Hmmm

Its a Megger 1552 (one of the last ones). So at least a couple of years old now.

I do have slight issues nulling them - but then I always found Meggers difficult to zero reliably. However in every other way, I dont dispute the test results that I get.

Have you experienced problems with old leads
 
to check leads set MFT to continuity setting connect 1 lead to both connections of instrument and if the resistance is all over the shop the probably lead or the socket tube of the tester as this was happening with my megger MFT
did you register online and get 3 yr warranty if so contact megger and they replaced all my leads even the 13A 3 pin plug adapter lead
gave me new detachable probe tips better than the plastic ones that came with instrument and they calibrated all for free
i even got a new extra set as the green new lead was damaged so they sent me a extra set
 
Last edited:

Reply to High ring test results at socket outlets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K
I am in training and decided to do some dead tests using my second hand Fluke MFT 1653B on an upstairs ring. I did the tests at a socket rather...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock