109
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
 
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
Are the sockets in question spurs?
 
Did you test between line and neutral as well. Have you confirmed they are not spurred.
 
The property is a bungalow with the cable drops coming in from the loft. The socket with the highest value has the ring coming in from above, and the cable looks to be original.
 
I had a job this week, where I removed some diy work on what I thought was an RFC in an existing extension. Well I thought it was an RFC, but in fact it was fed via a spur from another RFC.
 
how many cables was at this socket ? you posted you had done end to end at consumer unit (assumed) what about r1 + r2
The socket with the highest reading had 2 x 2.5 T&E. Took L-L, N-N, E-E reading at the consumer unit. r1 + r2/4 + Ze = 0.82 Ze was measured at 0.14. The calculated Zs of 0.82 was very near what i was getting all around the ring. 2 sockets were a bit lower (0.45 & 0.55) and apart from the 2 that were high, the rest were virtually spot on. ( My end to end values were L=0.92 N=0.92 E=1.83)
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock