not a problem was worth a check, I had just run in the new supply myself & tested.Sorry for asking the obvious, you never know when you might get a dodgy one.
What 400 ohmsWell if you are getting those sort of insulation resistance readings it no wonder the tub is tripping out. What is actually tripping CB or RCD?
Sorry mis read the OP didn't see the M after 400, reminder go to specsaversWhat 400 ohms
No Marc I misread your post, thought you had said you had measured 400 ohms IR missed the dirty great capital M, sorry for any confusionHi Pete
VIR
230 V
10.3 I
23.3 R
sorry am I having a blond moment heater is 2.5kw.
400M ohms IR test to earth good
23.3 ohms heater continuity
did you spot something that in the above that I may have missed ?
hi think it was Aqua spa but will check when I go back thanks, probably tomorrow if the rain stopsWhat make is the tub and the control equipment?
no problem, I thought I had missed something really obviousNo Marc I misread your post, thought you had said you had measured 400 ohms IR missed the dirty great capital M, sorry for any confusion
thanks will ask tomorrow when I am going round to take a look at the restJust re read the OP and noticed it is second hand do you know what chemicals the previous owner has been using, if it was chlorine then you may find that a seal has rotted and leaking water into something when it is running
Bromine is much more friendly and doesn't cause as much damage as chlorine
at this rate you'll soon be able to boil a kettle on the leakage current.30 mins in 87.5ma
Hi telectrixat this rate you'll soon be able to boil a kettle on the leakage current.