homesafe

Ive got a hot tub to wire one day this week,it requires a 32amp circuit and it is about 20meters from house,should i just run a 4.0mm armoured from the crabtree starbreaker to a IP65 rotary isolator,and then just use some armoured flex from that to the hottub,:eek:
 
Last edited by a moderator:
Just a couple of things I guess you would have thought of.
Obviously the circuit will need RCD protection, either from a shared incomer, if a split board, or an individual RCBO. If you are going across a garden be careful with your cable routing, garden forks will go straight through SWA (another reason for the RCD). No problem with the local isolator but if you have any SWA left over why not connect in with that or if not possibly SY. Remember to include for outdoor glands in your price.

Good luck, and remember to take your overalls off before you test your work:eek:
 
And don't forget, the steel wires on the swa are a consductor for the e f l path, AS well as the cpc(16th ed,sorry, what was the 17th term for the cpc?)
 

Reply to hot tub in the Canada area at ElectriciansForums.net

Similar Threads

Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K
Upgrading the Hot Tub to a Swim Spa, current power for the hot tub is 6mm 3x core swa to a 40amp mcb and 40amp rotary isolator. Cable is clipped...
Replies
9
Views
1K
Hi I am thinking of putting in a Hot Tubat the end of our garden, fed from the a garden shed, more or less next to it, now this might be a silly...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock