Discuss How many computers to 1 30ma rcd in the UK Electrical Forum area at ElectriciansForums.net

None I would remove the RCD and use a MCB, however if an engineer told me I had to keep the silly thing I would have no more than 4 max on it, if a printer on the circuit then 3 and not 4.
 
If they are insistent on rcd protection then fit rcd sockets rather than an rcd or rcbo at the db. The earth leakage from 4,5,6 computers depending on efficiency and age can trip them very easily
 
Once had to fit a dedicated RFC for computers in a school. Told the guy who designed it that he was being silly putting it on an RCD and was overruled. What the hell did I know, Just a bloody sparky were pretty much his exact words.
When the RCD wouldn't hold I didn't laugh (much)
 
If you MUST use an RCBO or RCD use at a minimum a type A or preferably a type B.
 
Rcbo is an rcd just with built in overload protection so basically an mcb and an rcd rolled into one so it will be rated at a certain mA as well.
 
If they are insistent on rcd protection then fit rcd sockets rather than an rcd or rcbo at the db. The earth leakage from 4,5,6 computers depending on efficiency and age can trip them very easily

And if the final circuits didn't meet with the 50mm buried depth rule?? If were talking about a shed load of computer work stations over several circuits, fitting RCD sockets is going to bump the cost of the installation way up there. Personally i use the rule of 5 computer orientated loads eg, PC, Printer, Scanner etc (or 3 X double sockets).. per 30mA protected circuit. Can't say i've ever had any nuisance tripping problems to date....
 
Instructed to put computer sockets on rcd,32amp,30ma,we usually put 7 twins on ring,using 2 terminal earth's connections,no problems whatsoever .Its a college & installed this method in all IT rooms ,cheers
 
Instructed to put computer sockets on rcd,32amp,30ma,we usually put 7 twins on ring,using 2 terminal earth's connections,no problems whatsoever .Its a college & installed this method in all IT rooms ,cheers

I assume you mean 32A RCBO's and not one 30mA RCD looking after several ring circuits feeding IT equipments?? We use 16A radial circuits for computer workstations with a ringed or if you like an additional CPC....

All such IT installations should be wired using the high integrity earthing arrangements.
 
Last edited by a moderator:

Reply to How many computers to 1 30ma rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
7
Views
507
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
716
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
991
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock