Have an install where a professional pressure washer is popping the fuse on start up.
The circuit is a 16a Radial from board to garage approx 15m long all fed by 2.5mm.
The washer is a commercial 1 phase unit and has the auto start and stop once the trigger is pressed as soon as the owner starts the machine the mcb pops out.
Washer is 2.8kw so 12a - the fluke says its pulling 11.35 when running but the inrush current is nearly 50 amps for a split second.
Will changing the MCB to a C curve 20amp cope for the split second (board is crabtree starbreaker so c curve is all I can go upto).
It works perfectly when plugged into a 32A ring.