dazj90

-
Reaction score
3
I'm installing a few extra lights to an existing lighting circuit in an office.
The existing lighting circuit is supplied from a BMS Control Panel, which has a number of lighting output sockets wired up to a contactor.

I'm going to be connecting the new lights up to one of the spare sockets on the control panel.
Would this warrant a certificate as the control panel is already connected to the mains DB?
 
if the BMS controller is fed from a single OCPD in DB, then I'd class it and it's associated lighting "circuits" as 1 circuit, therefore a MWC, IMO.
 
BMS Control Panel is fed from a fused spur (13A) which is fed from a 20A Type C MCB.
On the Minor Works certificate, what protective device would it state, the fuse or MCB.

Reason I'm asking is that the Zs value of the new lighting circuit is 1.69Ω which is ok for the fuse but not for the MCB (unless the MCB is changed to a Type B)?
 
The circuit after the fused spur is protected by the 13A BS1362 and so you can use the maximum Zs for the fuse as the limiting factor for the circuit part you installed. So long as the Zs complies for the circuit section up to the fused spur.
 

Reply to Installation cert/Minor works/Neither in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock