Discuss Installing sockets in loft, wiring query in the DIY Electrical Advice area at ElectriciansForums.net

Agree with others about getting an electrician in to do the extra sockets, but are you sure putting computer equipment in a loft is a good idea . my loft at the moment is about 55 degrees C , :sweat: so you will probable need some air conditioning units in there as well !

Or some windows :)
 
If you take power from an existing Lighting cable & start using it to power computers etc, the cable will in all probability overheat and may well catch fire.
The minimum this will do is severely damage your property, which your Insurance won't cover.

Can't say I agree with this, the most it's going to do is trip the breaker due to overload. Can't see how a 15-20A cable on a 6A breaker is going to catch fire (assuming of course a typical domestic lighting circuit)
 
I think a point was being made @hightower - you wouldn't tap a power circuit with 13amp outlets on a 6 amp circuit so just go with the warning posts - which they are intended judging by the OP attitude.
 
Can't say I agree with this, the most it's going to do is trip the breaker due to overload. Can't see how a 15-20A cable on a 6A breaker is going to catch fire (assuming of course a typical domestic lighting circuit)

So you'd advocate someone connecting, sockets to a lighting circuit ?
Don't know how long you've been around this industry, but I've been around it long enough to have seen the aftermath of doing so on more than one occasion. Trust me it's not pretty.
 
So picture the scenario - you are up in the loft playing with your raspberry pi (still don't know what one of them is!) and the breaker goes due to the overloading that you've placed on the lighting circuit because you took the easiest route and spurred off the lighting circuit in the loft. No strong stairs, you have to manage yourself down the rickety loft ladder WITH NO LIGHTS 'CAUSE THEY'VE TRIPPED and reset your breaker - mmmmmh!
 
So you'd advocate someone connecting, sockets to a lighting circuit ?
Don't know how long you've been around this industry, but I've been around it long enough to have seen the aftermath of doing so on more than one occasion. Trust me it's not pretty.

Please show me where I've said such things? My post was merely in disagreement with what you said the outcome would be. A properly designed lighting circuit isn't going to burst in to flames - that's literally the first thing you learn at college. However, I agree with what everyone else has said about a dedicated circuit (or jumping off a more suitable circuit), I just disagree that (untrue) scare-mongering is the way to advise the OP to get a professional in.
 
It's not scaremongering at all, fact seen it happen. Please don't insult me by trotting out the MCB will stop that happening, that's a crock.
When the op's 6a ? MCB has cleared an overload on multiple occasions then welded it's contacts together, ergo can't clear an overload. What happens then ?.

Anyway as far as I'm concerned, conversation over & done with.
 
if an attic is insulated properly, i.e. between the roof rafters instead of on the floor, then the heat in summer is vastly reduced, and it doesn't freeze in winter. double bonus.
 
if an attic is insulated properly, i.e. between the roof rafters instead of on the floor, then the heat in summer is vastly reduced, and it doesn't freeze in winter. double bonus.

I'm a bit dubious about this new fangled insulation between the rafters .... just think about all the cold air venting the roof space..

Our extension was insulated between the rafters... and open to the existing lost which has the old itchy stuff ..... so I added the itchy stuff in the extension...... and I know the new part does get blxxdy hot in the summer too!
 
It's not scaremongering at all, fact seen it happen. Please don't insult me by trotting out the MCB will stop that happening, that's a crock.
When the op's 6a ? MCB has cleared an overload on multiple occasions then welded it's contacts together, ergo can't clear an overload. What happens then ?.

Anyway as far as I'm concerned, conversation over & done with.

What happens if the MCB fails on a circuit that can easily be overloaded by design, such as a socket circuit? So do we need to start lashing in 16mm twin and earth just in case?
 
What happens if the MCB fails on a circuit that can easily be overloaded by design, such as a socket circuit? So do we need to start lashing in 16mm twin and earth just in case?
Have some trouble getting 2 16mm2 in a socket HT (JOKE)
 
One might have to consider installing cables with a higher ccc, such as the picture the OP first posted, reg 523.9.

Appendix 15 gives informative guidance on cable size selection for ring final & radial circuits.

Reg 433.1.204 states 'accessories to BS 1363 may be supplied through a ring circuit......The circuit should be wired .........with a minimum csa of 2.5mm (except MI)'. Can't find a similar reg for radials, but guess there must be.

Seen cheeky single sockets, blagged of the first floor lighting, to power the aerial booster, but somebody could plug in a 3kw, for their 'hydroponics' :)

So when would that 6a mcb trip, and what current would flow through the de-rated cable?
 
An overload is an overload, doesn't matter if it's because too many lights on the circuit, or because a 13A socket outlet is installed off it. If a 1.5mm cable feeding a light can deal with an overload while the 6A breaker begins to work, why wouldn't a 1.5mm cable feeding a socket outlet work the same way? I'm struggling to get my head around people's arguments on here.
 
Please show me where I've said such things? My post was merely in disagreement with what you said the outcome would be. A properly designed lighting circuit isn't going to burst in to flames - that's literally the first thing you learn at college. However, I agree with what everyone else has said about a dedicated circuit (or jumping off a more suitable circuit), I just disagree that (untrue) scare-mongering is the way to advise the OP to get a professional in.

But this circuit will not be a properly designed circuit once a DIYer has added sockets too it. And there's a pretty high chance that once they've tripped the mcb a couple of times they will solve the problem with a higher rated mcb.
 
An overload is an overload, doesn't matter if it's because too many lights on the circuit, or because a 13A socket outlet is installed off it. If a 1.5mm cable feeding a light can deal with an overload while the 6A breaker begins to work, why wouldn't a 1.5mm cable feeding a socket outlet work the same way? I'm struggling to get my head around people's arguments on here.

Yes the 6A mcb will operate the same regardless of what caused the overload.

But the common way a DIYer solves the problem of an mcb tripping through overload is to replace it with a higher rated one.

You also need to think about the size of the overload, the regulations require that we avoid the possibility of long duration small overloads as mcbs can't detect small overloads.
If the result of this additional socket is a load of 7A then it will take a long time to trip, but in all that time the thermal element in the mcb will be sitting there slowly cooking itself.

I think, and experience suggests, that small overloads damage mcbs more often than cables. Normally this results in an over-sensitive mcb but every once in a while it results in an mcb failing closed.
 
An overload is an overload, doesn't matter if it's because too many lights on the circuit, or because a 13A socket outlet is installed off it. If a 1.5mm cable feeding a light can deal with an overload while the 6A breaker begins to work, why wouldn't a 1.5mm cable feeding a socket outlet work the same way? I'm struggling to get my head around people's arguments on here.

Of course, I haven't got a outdoor socket for my deck lights, switched from inside on my downstairs lighting circuit :oops:
 
559 Luminaires & Lighting Installations. Reg 559.5.1 connection to the fixed wiring. At each fixed lighting point one of the following shall be used for the termination of the wiring system;
(i) A ceiling rose to BS 67 etc, etc, etc
(v) A suitable socket outlet to BS1363-2
(vii) A connection unit to BS 1363-4
:)
 
I think, and experience suggests, that small overloads damage mcbs more often than cables. Normally this results in an over-sensitive mcb but every once in a while it results in an mcb failing closed.

Well experience is something I can't argue against at this early stage in my career. And thanks for taking the time to explain it like that.
 

Reply to Installing sockets in loft, wiring query in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
428
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Replies
2
Views
987
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
627
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
600
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock