Was sent out to a job today to add in a hot water pump underneath a kitchen sink in a kitchen that had recently been done up. Took with me just a socket thinking that the electrician doing the kitchen work would have RCD'd it - but no. The woman had her own joiner do the work so I'm assuming he also got someone for the electrics or heaven forbid - done it himself. So, ended up just hard wiring the pump into an RCD spur. Anyway, I digress....
Before I fitted the spur I went to test the circuit - got ring continuity on all but noticed the N-N was 0.73 ohms and lower than the live which was 0.90 ohms. Earth - Earth was 0.61 ohm. R1r2 was 0.50 ohms.
Then, went to IR test between live and Earth, and neutral to Earth to find that it was showing 0.00?? I had everything unplugged bar a fridge and dishwasher which was built in and inaccessible but if anything would expect this to cause a live to neutral fault.
Has anyone experienced this before? I've seen it with RCDs on the circuit that have gone undiscovered but again it's usually L-N. Earth loop was OK as it was 1.01 ohms. Was definitely the correct neutrals and earths disconnected at board too.
I will jot this down on the MW sheet but would like to back it up with possibilities as to why. Obviously there is not a dead dead short across all or the circuit would simply not be working.
Thanks and loon forward to hearing the responses.
Ps - does anyone else really not like the new tapatalk layout for this? It's horrible.
Was sent out to a job today to add in a hot water pump underneath a kitchen sink in a kitchen that had recently been done up. Took with me just a socket thinking that the electrician doing the kitchen work would have RCD'd it - but no. The woman had her own joiner do the work so I'm assuming he also got someone for the electrics or heaven forbid - done it himself. So, ended up just hard wiring the pump into an RCD spur. Anyway, I digress....
Before I fitted the spur I went to test the circuit - got ring continuity on all but noticed the N-N was 0.73 ohms and lower than the live which was 0.90 ohms. Earth - Earth was 0.61 ohm. R1r2 was 0.50 ohms.
Then, went to IR test between live and Earth, and neutral to Earth to find that it was showing 0.00?? I had everything unplugged bar a fridge and dishwasher which was built in and inaccessible but if anything would expect this to cause a live to neutral fault.
Has anyone experienced this before? I've seen it with RCDs on the circuit that have gone undiscovered but again it's usually L-N. Earth loop was OK as it was 1.01 ohms. Was definitely the correct neutrals and earths disconnected at board too.
I will jot this down on the MW sheet but would like to back it up with possibilities as to why. Obviously there is not a dead dead short across all or the circuit would simply not be working.
Thanks and loon forward to hearing the responses.