Hi mate, get yourself trainee access on the forum
As for this quote above, IR testing doesn't prove continuity. Let's take a perfect circuit that max the IR reading out:
Switch 1 on, switch 2 off: reading >1000
Switch 1 on, switch 2 on: reading >1000
Switch 1 off, switch 2 on: reading >1000
Switch 1 off, switch 2 off: reading >1000
As you can see, you've proven the IR on each cable run but it doesn't prove any form of continuity. If there was a break in a strapper you'd still potentially get the same IR results. To prove continuity, you need to do a continuity test - there's no shortcut.
Yeah get what your saying all I wanted to know was could I incorporate the IR test to prove my light switches work both ways and all I get is flipping hassle
As for this quote above, IR testing doesn't prove continuity. Let's take a perfect circuit that max the IR reading out:
Switch 1 on, switch 2 off: reading >1000
Switch 1 on, switch 2 on: reading >1000
Switch 1 off, switch 2 on: reading >1000
Switch 1 off, switch 2 off: reading >1000
As you can see, you've proven the IR on each cable run but it doesn't prove any form of continuity. If there was a break in a strapper you'd still potentially get the same IR results. To prove continuity, you need to do a continuity test - there's no shortcut.