Hi mate, get yourself trainee access on the forum

Yeah get what your saying all I wanted to know was could I incorporate the IR test to prove my light switches work both ways and all I get is flipping hassle

As for this quote above, IR testing doesn't prove continuity. Let's take a perfect circuit that max the IR reading out:

Switch 1 on, switch 2 off: reading >1000
Switch 1 on, switch 2 on: reading >1000
Switch 1 off, switch 2 on: reading >1000
Switch 1 off, switch 2 off: reading >1000

As you can see, you've proven the IR on each cable run but it doesn't prove any form of continuity. If there was a break in a strapper you'd still potentially get the same IR results. To prove continuity, you need to do a continuity test - there's no shortcut.
 
The point of the 'global' insulation resistance test, is just a check to see if there are any issues that would require further investigation.
It will not prove continuity or polarity of lighting switches and wiring.
 
Thanks for your help,
So basically I'm gonna test the whole consumer unit, Main switch off, all breakers on, I'm gonna put a link in the outgoing side between L+N, the 2 way lighting circuit will have both light switches turned on, then once this is done I'm going to test between link and Earth Whilst also test while flicking both 2 way light switches on and off this will prove the insulation resistance in my light circuit?
Cheers
 

Reply to Insulation resistance test help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
308

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock