Discuss Insulation Resistance Testing Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

Djlelectrical

Been to a Job this morning problems with RCD tripping, Global IR came back 0.016, Split circuits down and lighting tested (Including outside tested 0.018) however tested again 0.567 and then 1.03 each time the figure increases until it sits about 1.14. Testing done L&N - cpc and then N-Cpc (Highest reading given)

The offending circuit has outside lights which are Energy saving.. I am concerned about the testing tho. From first its a fail and then after a few hits its a pass (Just I know) but which reading would you take and is the an explanation to why the figures are increasing.. Its only a case for this one circuit..

Havant had time to split the circuit down to narrow it down due to the results fluctuating
 
Usual culprit of an increasing IR is damp.....as the small current can actually 'dry' out the damp for a short period...try it at 1000v as long as you are not going to fry anything,sometimes it stays low at 1000v which helps with the tracing it process.
 
Check for water ingress in the outside lights. I had a similar problem, but there was no rcd, it was the mcb that kept tripping intermitantly. Opened the back of the outside light and water peeeed out. Just a thought. Could also be the cable that feeds the outside lights are damp. Could be a few things but with a reading below 2 Mohm, I would be investigateing furhter


Jay
 
You didnt mention testing between L & CPC.... if you did, what was the result?

Jay

I didn't test between L & CPC, tested L&N - CPC and N-CPC .. L&N - Cpc would show up a fault in L-CPC..

Never had a test result fluctuate so much, The damp suggestion seems feasible and would explain everything.. Especially why its tripping..

- - - Updated - - -

Now who else always moans I'm far too quick?......Oh yes,the missus.

Dont they all.. Well not when im haveing a quick beer with my mates..
 
I didn't test between L & CPC, tested L&N - CPC and N-CPC .. L&N - Cpc would show up a fault in L-CPC..

Never had a test result fluctuate so much, The damp suggestion seems feasible and would explain everything.. Especially why its tripping..



If you have installed cables in a wall and the muck chucker has been in and done his bit, if you done an IR test on them cables and hold the test button, you will find it will keep increasing. Ive sat there sometimes holding the button for a few minutes just to get the reading to >299.

Costs loads in new batteries though..lol


Jay
 

Reply to Insulation Resistance Testing Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
985
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock