Is this right anyone?
So basically I'm gonna test the whole consumer unit with an insulation resistance test rather than every circuit would you do basically I need to show my college and I've only been testing since last week and need to show an insulation resistance test of the whole board and show I can do it and prove my lights have no dead shorts and go off and on is this right? Main switch off, all breakers on, I'm gonna put a link in the outgoing side between L+N, the 2 way lighting circuit will have both light switches turned on, then once this is done I'm going to test between link and Earth Whilst also test while flicking both 2 way light switches on and off this will prove the insulation resistance in my light circuit?
Cheers
 
A global insulation resistance test on a consumer unit will check that there are no potential failures of insulation from live conductors to earth for all circuits.
The consumer unit should be switched off at the main switch with all MCBs on and the consumer unit checked for dead.
A link between line and neutral within the consumer unit is applied and an insulation resistance test from the linked Line and Neutral to the Earth bar is performed.
Any two way switches should then have one of the switches operated and the test repeated and then the other switch operated and the test repeated.
The lowest measurement should be greater than 2M ohms.

The test will not test if the light switches go on and off, this would have been covered during the R1+R2 testing or through polarity testing.
 
Don't forget the "Safe Isolation Procedure" when you turn the Main Switch OFF

 

Reply to Insulation resistance in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
591
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
435
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
488
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock