Discuss Interesting EICR ,Quote required in the UK Electrical Forum area at ElectriciansForums.net

Flanders

-
Esteemed
Arms
Reaction score
965
Was sent a EICR report the other day to quote the remedial work. Just thought I would share the highlights with you .
This is a school and all observations were code 1 or 2s
------------------------------------------------------------------

Lighting Circuits require further investigate for ethnic continuity

RCBO for shed must be hanged for amcb - RCD Confict



For all lighting circuits in all fuse boards DB1-DB5 if not RCD o RCBO protected.

All sockets circuits protected by MCB 32A in all fuse boards DB1 – DB5 if not RCD or RCBO
protected.


In this report “bath or shower” means special location such a toilet or other rooms where metal pipe
can be reach form power point.
For all hand dryers and water heaters located in the school.

All circuits supplied equipment in the toilets, boiler room connections, water heater if not protected
by RCD or RCBO.

-------------------------------------------------------------

The Report was done by a NAPIT Registered Company
I have advised the customer a site visit will be required to try and find out if anything was actually inspected properly o_O

 
I didn't realise RCBOs that feed sheds should now be hanged - no doubt this will cost us even more money if we have to buy MCB hanging kits. I tried my local CEF and they haven't even got them in yet.

Ethnic continuity is a new requirement in the 18th edition regs, which are being made more politically correct.
 
If they hang RCBO's, what do they do to RCD's ?

I know I'm gonna regret asking this, but what in the name of God is Ethnic continuity ?

Don't know about doing EICR's on schools, whoever wrote that needs to go back to school.

It's probably an auto-corrected 'earth continuity' but whoever did the report didn't know enough to spot the error.
 
It's probably an auto-corrected 'earth continuity' but whoever did the report didn't know enough to spot the error.
I think It was more to do with the inpectors first language not being english , I have framed the quote about no ethnic continuity and put in on my notice board , it my favoutite observation ever , just wish there was a reg number for it . Its also bugs me the amount so called electricians think a toilet is a special location , and insist hand dryer have to be rcd protected:mad:
 
I think It was more to do with the inpectors first language not being english , I have framed the quote about no ethnic continuity and put in on my notice board , it my favoutite observation ever , just wish there was a reg number for it . Its also bugs me the amount so called electricians think a toilet is a special location , and insist hand dryer have to be rcd protected:mad:
Whatever the reasoning behind the poor English, the information provided in the report is still a joke.
 
Whatever the reasoning behind the poor English, the information provided in the report is still a joke.
Yes exactly my thought too , Im not claiming to be the best a spelling and I myself have made the odd comical mistake but telling a customer that no rcd protection for circuits in a toilet is a code 1 is just plain incompetence
 
Not so much spelling as saying the wrong word , I used to do some work now and then for an old chap who was great but one day he left me to it saying he had to pop to the chemists to collect a 'description' for his Mrs, and another time when I'd 1st fixed his 2 storey extension said he'd get the itchy loft installation in. Best one though was the well to do customer who created a home cinema with a very fancy sound system and kept going on about the positioning of the 'large woofters' , I never corrected him because it was hilarious. :D
 

Reply to Interesting EICR ,Quote required in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
722
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
3K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock