Discuss Intermittent Fault - 20 characters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hightower

Been having an intermittent fault at home now for a few months. All RCBO board, wiring 3 years old.

Upstairs socket RCBO trips sometimes, maybe once or twice a week. Always seems to be when we turn something on, for example a light, cooker hood, oven etc. I'm thinking there's a dodgy appliance on the upstairs sockets, probably an extension lead, that's creating an intermittent N-E fault. Haven't tested anything yet, I'm sure you all know how it is with jobs at home... I think I'll be beginning with a PA Test of appliances when I get time, but just thought I'd post up here to see of any theories?
 
Have you checked the connections at the RCBO?

Can you leave most of the items unplugged?

Got any water leaks?

Hung any new pictures recently?

Have you ramp tested the RCBO?

Have you ir'ed the circuit?

Have you clamped the tails?

Is the kettle working?
 
Something this is permanently plugged in is almost certainly creating a permanent leak, not enough on its own to trip the RCBO, then when another device which also on its own isn't enough (and even cumulative with other similar devices) wouldn't normally cause the RCBO to trip, is not enough to push it over.
You could do an IR test across the circuit with everything that can be safely left plugged in and then work through socket by socket.
 
I've been putting it off because I know it's not gonna be a ten minute job. I even have an inkling what's causing it - an extension lead that is plugged in behind a massive bed that needs dismantling to get at. Oh well, job for the weekend, or maybe even bank holiday weekend since it'll be raining then by default anyway.

I'll update the thread when I do get round to it, but don't hold your breath
 

Reply to Intermittent Fault - 20 characters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
761
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock