Is 4mm heat resistant cable okay for 7.5kw range cooker?

Discuss Is 4mm heat resistant cable okay for 7.5kw range cooker? in the UK Electrical Forum area at ElectriciansForums.net

chris140

DIY
Reaction score
10
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind the cooker. He put this size in as I didn't know what size cooker I was going to be getting.

I ended up getting a 7.4kw range cooker and the electrician has connected it with 4mm heat resistant cable instead from the cooker to the back plate, instead of 6mm. Is this okay, and is it okay with the 10mm cable and 32a fuse?

Thanks
 
as mentioned previously, you need to allow for diversity, you will not pull enough load to worry the 4mm2 cable you have
 
o ffs... did you deliberately leave those two tabs showing? You dirty old man
No, I opened up a new window just to wind you up!
Back to normality again!
1713551629634.png
 

Reply to Is 4mm heat resistant cable okay for 7.5kw range cooker? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock