  1. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    Hi,

    I was doing my r1+r2 tests on a lighting circuit yesterday in a 6 bed house over 3 floors. Approximately 20 points not including switches. Mainly pendants but some light bars etc and almost all LED or low energy halogen type bulbs. Closed circuit r1+r2 values range from 0.88 on ground floor to 3.06 on top floor.

    The lights all work ok. I believe I have found one pendant with a discontinuous earth not picked up on a recent EICR done by a 3rd party, which I will return to this week and fix.

    However, a couple of pendants were giving me values of over 130 ohms when the switch was open (light off), which I check as part of the polarity test.

    Can someone help me understand why these high r1+r2 values might be occurring?

    Thanks

    Chris

    IMG_4494.JPG
     
  2. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Have you carried out an insulation resistance test on the circuit?
     
    • Like Like x 2
  3. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    Ah yes, good question. I should have said.

    I have performed a R1+Rn - R2 insulation test and got 130Mohm. Not perfect but acceptable. R1 - R2 has not been done as yet because I don't want to have to remove all the bulbs!
     
  4. DPG
    Offline

    DPG Electrician's Arms

    Location:
    S Yorkshire
    Are you confusing readings somewhere? You mention a continuity reading of 130R and an IR reading of 130M. Is it just coincidence you have similar results? (I know they're a factor of a thousand different, bu tyou know what I mean).
     
  5. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    You're reading through the lamps back to the neutral bar.
     
    • Agree Agree x 4
  6. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    No its just a coincidence. I've got two pendants its happening on. one is reading around the 130 mark and the other is at 150.
     
  7. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    Can you explain what you mean. Sorry.
     
  8. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    Turn the switches on, why have you got them off. You have lost the R1 return at the light with the switch off.
     
  9. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    You misunderstand. This is for just one of the two problem pendants. With the switch closed/on I'm getting 2.89ohm but with the switch open I'm getting 150ohm when I would expect to see >2000ohm (open circuit) as I do for all of the other pendants.
     
  10. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    Do you have all the lamps removed.
     
  11. CDB
    Offline

    CDB Active EF Member

    Location:
    UK
    Nope but I'm using the same method on another 18 pendants on the same circuit and getting open circuit when The switch is open/off. And many of them have the same model of bulb so why would these two be different?
     
  12. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    Do you mean R1+R2? r1 r2 and rn are for ring finals only
     
    • Useful Useful x 1
  13. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    Its hard to follow your description of what is your situation but here 's a try

    The only thing you are removing when you switch off are the switch live back to the pendant and the switch contacts
    If you are now getting 130 ohms where 1000s were expected,it seems to me it can only be via the open switch
    Have you measured the switch itself as a separate item
     
    • Like Like x 1
    • Useful Useful x 1
  14. static zap
    Offline

    static zap Regular EF Member

    Location:
    west midlands
    Comparing cold bulb and 130R ,just leaves heat damage ,
    causing tracking somewhere ,or another cause.
    Are the halogens 230V ,or is some 12V converter envolved .
     
  15. Wilko
    Offline

    Wilko Gorillas are Great Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Any 2 way lights in the mix?
     
    • Like Like x 1
Loading...
Similar Threads - Lighting Circuit r1+r2 Forum Date
high r1+r2 on lighting circuit Electrical Forum Jan 19, 2017
Domestic Lighting Circuit Methods In New Builds Electrical Wiring, Theories and Regulations Jun 18, 2017
5A lighting sockets circuit Electrical Forum May 20, 2017
2.5mm Lighting Circuit Electrical Forum May 15, 2017
Inductance on lighting circuit Electrical Forum May 11, 2017
Switch for entire lighting circuit? Looking for Domestic Electricians? May 8, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job