Discuss Lighting Circuit r1+r2 values. in the UK Electrical Forum area at ElectriciansForums.net

Are you registering voltage between line/earth at the light fitting and is the insulation resistance clear.

Obviously this is a dead test so if you are asking about 230v I have not looked.

But could I be picking up on Smoke/Heat alarms or Emergency Lighting?

But if that is the case then why are the other lights not seeing the same issue. Argh - my computer scientist brain likes consistency!

Thanks for the continued help by the way!
 
It isn't a problem I thought you meant ohms for when the switch was open. I assume you get 130 meg ohm when you IR test the whole circuit with all switches closed.
 
It isn't a problem I thought you meant ohms for when the switch was open. I assume you get 130 meg ohm when you IR test the whole circuit with all switches closed.
Yes 130 meg ohm for IR.

But either 130 or 150 ohm for the two problem pendants when switch is closed.
 
It is not a problem 130 meg ohm is well above what you require. Your picture indicates the wiring to be 50 odd years old and you would not necessarily expect an infinite IR reading especially on a lighting circuit, I would think no more of it.
 
It's not the IR that concerns me because as you put it the wiring is old and it's well above the minimum.

My question relates to the 130 OHM and 150 OHM I'm getting for the R1+R2 test on two different pendants when the switch is open. If the switch is open I should be getting open circuit or in my case >2000 ohm as I do with all the other lights on that circuit.
 
Are the switches relatively old as you could be getting dirt on the contacts at the switch tracking across or you may have leakage through lower insulation resistance
 
It is possible old, worn switches are the cause but I wouldn't have thought low ohms would pick this up but yes ditch the wiring from the switch.
 
Are the switches relatively old as you could be getting dirt on the contacts at the switch tracking across or you may have leakage through lower insulation resistance

Hi Ian,

Dodgy switches was my first thought. They are old.

To determine your second suggestion I guess I would need to do a full IR which is pretty difficult given the installation.

Switches first!

Thanks for the ideas.
 
Hi Ian,

Dodgy switches was my first thought. They are old.

To determine your second suggestion I guess I would need to do a full IR which is pretty difficult given the installation.

Switches first!

Thanks for the ideas.
Why is it difficult to do a full IR you can ignore the L/N test.
 

Reply to Lighting Circuit r1+r2 values. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
864
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
569
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock